Quote:
Originally Posted by Kentucky
"For my cooling scheme I plan to control the exhaust fan proportional to a temperature setpoint. The humidifiers will operate according to a humidity setpoint which I would increase on hot afternoons and then set lower in the evenings."
I see. I'm going to interpret your words above in strict control system language as opposed to everyday dictionary language. I believe that's what you mean.
|
Yes, I have a Phason MT4C proportional fan speed controller that will vary the fan speed from an idle setting at the temperature setpoint to full speed at 6 degF above the setpoint. The controller can be configured so that at 2 degF below the temperature setpoint it will turn off the exhaust fan or it can be configured to always run the exhaust fan at the idle speed setting when below the temperature setpoint deadband. I will probably use the Phason controller in the configuration that always maintains idle speed below the setpoint and add an on-off controller that will remove power from the Phason (and thus completely stop the exhaust fan) when I approach my heating setpoint.
http://www.phason.ca/mtc4c.htm
Quote:
|
Originally Posted by Kentucky
It appears to me that, unless you left something out, operating the fans on temperature control and the foggers on humidity control, will at times allow fogging without the fans running. Depending on the location of the humidity sensor, this could quickly shut off the foggers or maybe not. Nonetheless, operating the foggers with no fans decreases drop flight time and evaporation rates increasing the likelihood of rain in the GH.
|
No, I will be using an Aquafog humidifying fan as my first level humidifier.
http://www.jaybird-mfg.com/Directfeed_desc.asp
If I add a fog nozzle system it would be configured as a supplement to the Aquafogger so I would always have the Aquafogger fan running when humidification was active.